• 0 Votes
    3 Posts
    2k Views
    T
    @martin_triska Thanks a lot! I had to do some debugging due to incompatible base source deviceTree (which was ultimately resolved by patching the compatible directives and a bit of merging together), but your response helped a ton! It works like a charm, so again, thanks! We plan to open source parts of the project in the future as well (along with a stable release) ... so hopefully it will help someone else too :)
  • 0 Votes
    2 Posts
    2k Views
    Martin KudláčekM
    Hello @Martin-Freundl, first of all, you shouldn't apply 24V to a 0-10V input. There are 12.5V transils on the input, so you probably burned it. The voltage measurement happens between the AI input and the AGND. The AGND is not connected to any other GND. Thats why you didn't measured any voltage between AGND and 24V. Martin